Good Evening Victron Community,
I have installed a Multiplus II GX in a topology with all Non-Critical Loads upstream of the AC Input. Critical Loads on AC Output 1 as usual.
When installing the External current sensor on the Main Circuit and returning from an Outage the Inverter gave an Error 24 related to the backfeed relay.
Although the error makes sense to me regarding it seeing Current (from the external sensor) while it was expecting no current (Ac-In relay open) I would think that selecting the External Current Sensor Connected tick box in VEConfigure would tell it to ignore this discrepancy?
I have since removed the Current Sensor (and unticked the tick box) and have tested the exact same outage successfully without Error24.
Although this post mostly serves as a possible bug flag, I would like to end it with a question.
Would it be possible for me to install a three phase Grid Meter upstream of the AC Input and non critical loads (Carlo Gavazzi 65A) instead of the Current Sensor and still avoid this Error 24 Situation?
If yes, would I be able to add an unpowered USB hub onto the USB port to have both an external Wifi adapter and USB to RS485 adapter on the GX portion in order to connect the Grid Meter?
Kind Regards