2 Multiplus Inverter Fuse

I'm using two Multiplus 3000W inverters in parallel. What fuse size should I use for the main feed to both of them?

multiplus in parallelmultiple inverters
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

Each should be individually fused.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

cc5084 avatar image cc5084 commented ·

@nickdb Thank you for the quick response. Does this also mean I will have 4 main cables going from the batteries to each inverter then (2 hot 2 ground)?

0 Likes 0 ·
nickdb avatar image nickdb ♦♦ cc5084 commented ·

Generally you would use a busbar (Lynx or similar) to connect the DC end together. Much neater.

If you haven't previously, have a read of the wiring unlimited guide.