I'm using two Multiplus 3000W inverters in parallel. What fuse size should I use for the main feed to both of them?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I'm using two Multiplus 3000W inverters in parallel. What fuse size should I use for the main feed to both of them?
Each should be individually fused.
@nickdb Thank you for the quick response. Does this also mean I will have 4 main cables going from the batteries to each inverter then (2 hot 2 ground)?
Generally you would use a busbar (Lynx or similar) to connect the DC end together. Much neater.
If you haven't previously, have a read of the wiring unlimited guide.
Parallel, split- and three phase VE.Bus systems manual
Theory on wiring large systems PDF
Three-phase and parallel system theory training presentation
Three-phase & Parallel installation training video