Hi all,

I am currently finishing a new ESS installation with three MP2 5000, a Cerbo GX, mixed AC+DC coupling and a VM-3P75CT. Everything seems to be working quite fine so far, but the Cerbo doesn't find the VM-3P75CT, which is quite far away from the rest of the system and connected via Ethernet.

Both devices are in the same (wired-only) Ethernet. Both obtain IP addresses via DHCP without any issues. I can ping both devices without packet loss and with the expected low local round trip times <1ms. In Wireshark I can see the periodic MDNS messages of the VM-3P75CT, announcing its presence on the network. But still no trace of it on the Cerbo.

I therefore also checked with Victron Connect. Victron Connect can see both the Cerbo and the VM-3P75CT. The latter also shows plausible measurement data in Victron Connect.

Victron Connect offered an update for the VM-3P75CT, which I did. It now reports being at firmware v1.06 with Bootloader v1.04. No improvement after the update.

Does anyone have an idea where to look or what to try? Thanks! :-)

Cheers

cerbo gxvm-3p75ct
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
andrii-podanenko avatar image
andrii-podanenko answered ·

You need to upgrade you Cerbo GX firmware to latest one

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bjscheue avatar image bjscheue commented ·

Thanks for the hint. Strange, because I am certain that I triggered a Cerbo GX update very early during my installation. But anyway, seems it wasn't up to date, and certainly that did the trick. :-)

1 Like 1 ·
andrii-podanenko avatar image andrii-podanenko bjscheue commented ·

also to upgrade meter firmware - there are some issues fixed

0 Likes 0 ·
ldoes (Victron Energy) avatar image
ldoes (Victron Energy) answered ·

Hi @bjscheue, if you can see the VM-3P75CT in Victron Connect, it means that the GX device can communicate with it.

Have you followed the steps under GX device monitoring on page 8 of the VM-3P75CT manual? You need to enable the VM-3P75CT under Modbus devices before it is visible in the device list.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bjscheue avatar image bjscheue commented ·

Hi,

thanks for the swift feedback. Yes, I followed these steps - as far as possible, that is. That's exactly where the problem is: The GX device doesn't show the energy meter. No Modbus TCP devices discovered on the Cerbo. A manual scan doesn't help either.

0 Likes 0 ·
Show more comments
dwmarine avatar image
dwmarine answered ·

Had exactly the same issue, agree with Andrii, this fixed it.

2 |3000