Are there any way, to make an grid lost audible alarm on MultiPlus-II GX using some of analog outputs, or aux relay?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Enable grid loss monitoring and the GX audible alert in GX settings.
You can make it only with CerboGX, if i'm no mistake. Multiplus GX general tab has no "audible alarm" parameter
Multiplus 2 gx doenst have an audible alert, you can use the relay with an assistant for this, and then connect what ever you want for alarm on the relay contact