Can I set ac out 2 to not discharge the batteries on a Multiplus-II?
I want to connect a Zappi EV charger through the system so that the VRM registers the total consumption, but I don't want the EV to discharge the batteries?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Can I set ac out 2 to not discharge the batteries on a Multiplus-II?
I want to connect a Zappi EV charger through the system so that the VRM registers the total consumption, but I don't want the EV to discharge the batteries?
By default, the AC 2 output is active whenever the grid is connected at the AC input. Power assist would go active if the AC 1 + AC 2 loads exceeded the AC input current limit. The AC 1 and AC 2 output currents are not measured separately.
You could connect the EV charger before the Multi and insure the current probe is either not used or connected between the tap to the EV charger and the Multi input. This way the Multi would never supply power to the TV charger.