Cerbo Relay 2 + SolarEdge analog power reduction

Hi

I need help with the of relay 2 which is available min. from vrm to control the switching off of SolarEdge inverter. it so happens that i have two PV inverters: Fronius on AC out2 and SolarEdge on AC IN.SE I would like to turn off when there are negative energy prices to not give back to the grid. I made a cable that on the cerbo side I put in NC GND contacts and on the SE side L1 V. Clicking on VRM relay 2 unfortunately does not turn off the SE. Maybe something needs to be set in the software settings on the inverter itself. please help.

cerbo gx
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pwfarnell avatar image pwfarnell commented ·

This is a Victron forum so we can not help on the settings for the Solaredge PV inverters unless someone has direct experience.

One thing you might like to check is the Cerbo relays are volt free dry contacts, meaning they are only a switch. Does the terminal on the PV inverter need a +12V or 0V signal to work or should it work with dry contacts., If it does need a signal voltage then you need to pick up a 12V or 0V supply.