Hi there, we did an installation (VRM id c8df84cacf23), with:
16x REC N-Peak 315w
1x 150/45
1x 250/100
1x Multiplus II 5000VA
BYD-Box 10kWh
70mm2 battery cable (1,5m each)
All the loads are at the AC-Out, as the customer wants backup for everything.
"Off-grid" works perfectly for days, no problem. But with mains connected at the AC-in, there are problems running ESS .
What happens is that randomly (but it seems to happen mostly when loads are about ~2000w with the microwave on). Lighting starts blinking, so appliances go off (TV for example), and everything comes from the grid, then after some seconds the problem stops.
You can check this behavior here for example (customer . made monitoring system) : Out voltage (green line) goes down a lot (actually this is an average, it actually blinks), and it starts taking from the grid (red fill graph). There's no error coming at all.
We checked the wiring, its brand new 3G6mm2, about 10m from to the inverter). Everything works perfectly "off-grid", or with the grid physically bypassing the inverter. With ESS, it turns into a random mess. Yesterday it even gave an overload error at 21:09, with only 2500w load.
Grid voltage is fine, frequency its fine, house runs perfectly with either only grid (bypassing the inverter with a switch), or off-grid, running from the inverter only.
Right now, its running off-grid mode, so it dont damage anything, but if you want I can tell the customer to turn on the grid, so you can check.
We also installed a similar system at the neighbour house (brothers), with a Multiplus II 3000 GX. We tried to mimic the same behavior, but no luck, even with ESS runs flawless.
Charge controller, Venus and Multiplus are all updated to last firmware version (actually it got worst with the last inverter update).
Checked all the wiring, and everything's fine.
Any help please?
Thanks