question

raspyroadie avatar image
raspyroadie asked

Easysolar max combined charge set

I have an easysolar 2 GX. What I would like to do is set the maximum charge current to 50a from all sources. Right now, it is maxing the solar at 50a and the generator at 50a. But if I have the generator running and the sun comes out, it will easily jump above 50a combined. I was hoping that it would combine the 2 to a maximum of 50a. I don't really want to turn off the solar every time I want to use my generator. I can set this on a chinese brand, but there doesn't seem to be a setting for this in the victron

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

With DVCC enabled, this can be set globally, but be aware it will be ignored if feed-in is enabled.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fideri avatar image Fideri commented ·
@nickdb

Does this apply to DC Loads only? Because the relevant part of the manual says:

Current drawn from the system by the inverter/charger is compensated for. For example, if 10A is drawn to power AC loads and the limit is set to 50A, the system will allow the MPPT solar chargers to charge with a maximum of 60A.

F.

0 Likes 0 ·
Show more comments