question

misullivan avatar image
misullivan asked

PowerAssist not happening on EasySolar new installation.

New installation and was told by the dealer the default configuration is no feedin but powerassist enabled.


It isn’t and I can’t seem to work out how to get it to work.


Can anyone help? I don’t have a USB to VE.Bus dongle so can’t use VEConfigure (and don’t have a windows machine at all so couldn’t use it anyhow) .. can’t login to the VRM portal so (assuming I have read everything correctly and VEConfig Remote is there) can’t use VERemote. (See my other post about not being able to use the VRM).


Thoughts? Solutions?


Thanks,


Michelle

VEConfigure 3powerassist
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Justin Cook avatar image
Justin Cook answered ·

@misullivan, a couple of questions: first, what is the condition that leads you to believe that PowerAssist isn't turned on? Every default config I've seen does have it enabled, so I'm curious as to whether your dealer accidentally turned it off, or if it had been previously modified, or if it is in fact on but you're expecting it to do something other than what it does...

Second, can you not contact the dealer from whom you purchased the unit and have them re-configure it? We're a Victron (and etc) distributor and we fairly routinely program Multis before we ship them out and/or provide programming assistance after the initial sale.

Third, though unfortunately I can't help you with your VRM issues, what kind of phone do you have? I know that the MK3 to USB adapter will work (using another Type A to Type C USB adapter in my case) on an Android phone to make a wired connection to the Multi and program it using VictronConnect on my phone... Multis cannot be programmed over Bluetooth, but with a wired connection to the phone, the programming functionality of the mobile VictronConnect is the same as the desktop version. I believe that this applies to iOS devices as well, but I'm not entirely certain of that because I don't have any, so have been unable to test.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

misullivan avatar image misullivan commented ·

Quite simply shown in the following...



If I throw the main breaker (AC In) you can see there is clearly enough PV power to run the essential load....



In all the docs and manuals I can’t see any settings for changing it without using VEConfig .. as for the dealer.. over 1000km away in Queensland... I’m 2 hours south of Sydney and they shipped to me from Melbourne..so everyone is at least 10 hours drive away and/or shipping away.



It arrived new in the box.

0 Likes 0 ·
image.jpg (2.2 MiB)
image.jpg (1.3 MiB)
klim8skeptic avatar image klim8skeptic ♦ misullivan commented ·

Some reading on how power control/assist can work for you. https://www.victronenergy.com/upload/documents/Book-Energy-Unlimited-EN.pdf Page 42 section 8.3

0 Likes 0 ·
misullivan avatar image misullivan commented ·

Oh, I’m in the VRM now and got the CcGX connected to it.. just as an FYI

0 Likes 0 ·
JohnC avatar image
JohnC answered ·

Hi. Those screenshots help. I suspect it's not a PowerAssist issue at all, just the onboard Multi charger overwhelming the mppt.

Good you now have VRM access, so you can now change the Multi charge settings. And if you set the Absorb and Float settings there to a little below those of the mppt, they'll both work, but the Multi will drop away first as it gives the mppt priority with the higher settings.

Note VRM won't let you alter mppt settings, but hopefully they're set on suitable defaults for whatever batts you have.

There may well be other approaches to this, but in deeper, darker territory, and perhaps not recommended for a novice (with respect) in early-learning-curve state.


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

misullivan avatar image misullivan commented ·

Very early learning curve, no probs admitting that, and to be honest this is the first time I've really felt like a clueless newbie in a long while... :) ... I expect to be an expert (well non-novice/experienced :P ) by the time I get to the next install :)


It just scares the hell out of me as it's an expensive bit of kit which could be very very dangerous if I screw up so very very careful settings and double checking/triple checking some things..


Thank *all* of you for your patience and knowledge sharing so far.


Michelle

0 Likes 0 ·
Show more comments
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

I think PowerAssist is not working like you think it is.

I think you want to use the power from PV to supply your loads instead of using the grid.

For this you have to setup an ESS-assistant

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

misullivan avatar image misullivan commented ·

I think you could be right... so is that in software or in external hardware?

0 Likes 0 ·
misullivan avatar image misullivan misullivan commented ·

Ok now I hit another wall ... firmware version for the inverter is 413.. next to be 416 or newer.. doesn't seem to be any way to online update that. USB-MK3 the only way?

0 Likes 0 ·
Matthias Lange - DE avatar image Matthias Lange - DE ♦ misullivan commented ·

ESS is software.

To update the FW of the Multi you need a MK3 because to initialize the update the Multi has to switched off an on again to update the bootloader.

Via VRM you can only update the FW of VE.direct devices.

0 Likes 0 ·

Related Resources

VEConfigure manual

VEConfig alternative method for VE.Bus using VictronConnect

Additional resources still need to be added for this topic