question

suavek avatar image
suavek asked

Venus GX relay to control a 5A 12V blower

Can I use Venus' built-in relay to control 5A 12V blower?

Venus GX - VGXRelaycontrol
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

No, I think that is to much for the relay of the Venus.

But you can use the Venus relay to control a stronger relay that can drive the blower.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

suavek avatar image
suavek answered ·

Thank you for your opinion, which is similar to mine. As I prefer to keep a circuit as simple as possible, I need the answer based on the data. In the Venus' datasheet, there is a limit of 6A 30VDC. I'm not an electrician, but I know that different types of loads have different properties and I want to be sure.venus-gx-datasheet-relay.png


6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Duivert NL avatar image Duivert NL commented ·

like matthias lange said, better use a power relay to protect your venus relay

dont forget to put a diode over the power relay coil to protect the venus relay contact

1719990333883.png


0 Likes 0 ·
1719990333883.png (58.8 KiB)
Fideri avatar image Fideri Duivert NL commented ·

@Duivert NL

Just a clarification on your drawing. I have seen many contrasting drawings. In yours, you have the diode across the negative and positive wires.

According to some sources, with such a connection, the diode only serves as a "bypass" diode, not a "blocking" diode. Such sources say that for a blocking diode function, one has to connect the diode along the powered line (positive only).

Or is it the other way round? I'm confused.

F.

0 Likes 0 ·
Alex Pescaru avatar image Alex Pescaru Fideri commented ·

It's correct how the diode is placed and its "polarity", but this diode snubber type is used to protect the silicon junctions that drives the relay coil from reverse currents, which are killers for transistors junctions.

For protecting (relay) contacts, which don't care about the sense of the current, generally, an RC type snubber is used, across the switch / relay contacts.

Or to accommodate both, use an RCD snubber. Which might be overkill... :-)))

0 Likes 0 ·
Fideri avatar image Fideri Alex Pescaru commented ·
@Alex Pescaru

Clear. I'm assuming that the logic is the same when using an external solid state relay or any other type?

F.

0 Likes 0 ·
Alex Pescaru avatar image Alex Pescaru Fideri commented ·

Yup. Although a SSR may have all these already inside.

0 Likes 0 ·
Fideri avatar image Fideri Alex Pescaru commented ·
Thanks
0 Likes 0 ·
Alex Pescaru avatar image
Alex Pescaru answered ·

Hi @Suavek

While the datasheet values are in range for your application, switching 60W through a small relay will not provide a long life for that relay.

The problem is the DC arcing, that is bigger and bigger as the load increases.

Successive arcing during time will lead to a slow destruction of the relay contacts and sooner than later the contact will either melt or fuse together.

Here's below a graph for seeing the cycle life of a high power DC contactor from Tyco.

You can clearly see, the greater the current (power), the less switching cycles.

So, if you want to protect something that's inside and difficult to replace, switch an external relay which is easier to replace.

Alex

ssr.jpg


ssr.jpg (133.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Fideri avatar image
Fideri answered ·

@Alex Pescaru and @Duivert NL, sorry to come back to you and for hijacking this thread but I think the OP will find this information useful.

Looking at the Amazon US site again, all the listed manufacturers say that their diodes should only be connected inline the positive side only (see attached photos). My tentative conclusion is that the wiring depends on the manufacturer. I searched for "schottky diode" and for "blocking diode". It seems Americans don't use the term "snubber".

Second question: which specific one would you pick? It seems the MD is an overkill. Its specs and link below. The second one has less capacity but it is cheaper. Link also attached.

1. MD

2024-07-02-diode-ex-sl1500-wiring.jpg

2024-07-02-diode-ex-sl1500-specs.jpg

https://www.amazon.com/dp/B0C8N7LQGN/ref=sspa_dk_hqp_detail_aax_0?psc=1&sp_csd=d2lkZ2V0TmFtZT1zcF9ocXBfc2hhcmVk

2. Generic

2024-07-02-schottky-diode-look.jpg


2024-07-02-schottky-diode-wiring.jpg


9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alex Pescaru avatar image Alex Pescaru commented ·

Hi @Fideri

I believe that you / we are talking of different things.

Those diodes you are talking about are for combining / isolating DC sources or bypassing PV panel elements when shading occurs.

They are high power/current diodes, not like those used for induction protection.

Like these from victron: https://www.victronenergy.com/battery-isolators-and-combiners/argo-diode-battery-combiners

Alex

0 Likes 0 ·
Fideri avatar image Fideri Alex Pescaru commented ·

We might be talking about different types. But according to their documentation, those quoted serve to prevent "reverse currents" and protect "junctions"from such power. They are not bypass diodes.

F.

0 Likes 0 ·
Alex Pescaru avatar image Alex Pescaru Fideri commented ·

Yes, they are... :-)))

In the end, a diode is a diode. Conducts electricity only on one direction and is used to protect devices, in our both cases, but for different purposes.

Only that in one case is a small current diode, in the other is a high current diode.

0 Likes 0 ·
pwfarnell avatar image pwfarnell Fideri commented ·
Diodes are like one way valves in pipes, if the voltage on the + side of the diode is higher than the voltage on the - side then current flows in the direction of the arrow. If the voltages are reversed then no current flows. You understand diodes.

If the snubber / back emf diode on the relay, normally it does not let any current through because the +12V is connected to the diode negative. However, when the switch (Cerbo relay) is opened, the magnetic field in the power relay collapses and generates a reverse voltage (back emf). This voltage can be very high, damaging the switch. The diode conducts the current resulting from the back emf because the back emf makes the positive output of the relay go negative. As the current passes through the diode, this stops the voltage over the switch getting too hogh so that the switch is not damaged.

0 Likes 0 ·
Show more comments
Fideri avatar image
Fideri answered ·

@Alex Pescaru and @pwfarnell

That's clearer. To be on the cautious side, I will buy 2 diodes and wire one in parallel and the other in series, if it has no negative effect. I know one of the diodes will be redundant but that is fine by me.

F.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Venus GX manual

Venus GX product page

Additional resources still need to be added for this topic