question

doublebubble avatar image
doublebubble asked

Different current draw

Asking for advice, we have 3 x 240ah lithium batteries connected together as per the crude drawing attached but this basicallywhat we have, all cables are 70mm2 and of the same length connected to busbars, I haven't shown the fuses but all batteries are individually fused also a 400amp T class fuse at the multiplus, all batteries are at the same state of charge I.e. 13.5v but I'm seeing a different current draw between battery one and the other two, as an example, battery one may have a draw of 0.31v as compared to battery 2 & battery 3 measure a draw of 0.16v, do I need to be concerned? or do I need to reconfigure some wiring.20240629-093437.jpg

inverter current draw
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

@doublebubble it's unclear if you are measuring voltage or current. confirm.

have you fully (and I mean FULLY) charged each battery?

0 Likes 0 ·
2 Answers
doublebubble avatar image
doublebubble answered ·

Thanks for the reply, just to be clear I am not an electrical expert, the batteries have been in for 10days now and when fitted all three were at 13.31v, I'm only measuring the current from each battery on their individual cables with a clamp meter, at every single connection from each battery, through the fuses to the multiplus all measure 13.5v, is my configuration of paralleling these batteries correct.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

@doublebubble Given your battery leads are all the same length, current should be about equal. As long as the cable lugs are clean, flat, free from burs and torqued properly.

all batteries are at the same state of charge I.e. 13.5v

Just because the batteries all read 13.5v, does not mean they are all at the same Soc. Differences between Soc can give different current measurements.

Hence the question, have you fully charged the batteries?


1 Like 1 ·
Show more comments
doublebubble avatar image
doublebubble answered ·

I need to revisit my original question as I'm still seeing a different current draw, as per the suggestions above I have gone through it all with no indication that there is an issue with the wiring/connections, yesterday I was running our hot water service which has a 1200w 240v element, measuring the current draw from each individual battery came in at no.2 & no.3 battery having a current draw of 20.2amps whilst no.1 battery had a current draw of approximately 12amps, can anyone shed some light on why? Should I be concerned? What is confusing is that after a couple of weeks into the use of the system it was the other way around with no.1 battery drawing twice as much as no.2 & 3 so for some reason that has reversed with no change in the set-up, could no.1 battery have an internal fault? Each battery has its own internal BMS.

Thanks in advance

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic