Hi all,
I get the Pre-charge error E-B25: The load resistance is too low to precharge the loads. Disconnect or reduce some DC loads.
My system is the following:
- 4 Victron Smart LFP batteries 200 25,6/200-a
2 parallel strings with two batteries in series
- Lynx Smart BMS 1000A
- 3 Quattro's
I see from the figure below that the precharge resistor is 47Ohm. At the moment of precharging the battery voltage is 53.5V. That makes 1.14A and 61W power dissipation at the inrush resistor. When I searched for this resistor on the internet I found that max power dissipation is 75W.
Does Victron measure inrush current and limits it? Is there perhaps a temperature measurement that trips? Does anyone know what these limits might be? It might be 1A?
Many thanks,
Simon