question

rvnomad avatar image
rvnomad asked

Inverter fuse concerns and recommendations for MultiPlus II 2x120V

My setup:

  • 50-amp RV with Onan 5500 generator
  • Renogy 400 watt solar panels with Victron SmartSolar controller
  • Battleborn 2x100 AH batteries
  • Victron MultiPlus II 2x120 inverter charger
  • Victron BMV-712 battery monitor.

I am troubleshooting a considerable voltage drop when running a microwave (150 Amp draw) and have found several sub-optimal details in the work done by the RV shop installer. This 300-amp fuse is installed between the battery (right terminal) and the inverter (left terminal). An IR thermometer shows that a spot on the fuse blade warms up to nearly 100 deg C!


inverter-fuse.jpg


The fuse is rated for 300 amps, but seems rather thin to be conducting such a load and has a voltage drop of about 0.2V across it. It is possible that the heat is coming from the cable and not from the fuse itself, but the cable lug does not heat up to the same degree.

My questions:

1. Is this kind of fuse appropriate? And is there a name for it?

2. Can I replace it with a push button circuit breaker like this one? (Example link: https://www.amazon.com/Hamolar-Circuit-Breaker-Manual-Holder/dp/B095YZN677 )

1718515787838.png

3. What should the fuse rating be? My highest typical load is about 160 amps from the two lithium batteries. Battleborn says that 200 amps is the normal current spec, with 300 amps for less than 30 seconds.

All suggestions are appreciated, especially for fuses / circuit breakers that are high quality and reliable.

Multiplus-IIfuses
inverter-fuse.jpg (241.1 KiB)
1718515787838.png (283.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
pwfarnell avatar image
pwfarnell answered ·

Do NOT use one of those breakers you show, there are many reports on this site of people having high resistance on them melting bodies, tripping at the wrong currents etc.

You do not state what type of Multiplus you have, a 3000VA model should be fused with 400A and should have 2x50mm2 cables. I do not like that type of fuse holder with the allen key (hex key), i am not sure that you can torque it up enough. Also, the indicated hot connection does not have a washer under the bolt head, this is very important as without a washer the tightening torque is much less effective and that will make the connection contact poor. Change the bolts to proper hex head brass bolts with washers and torque them up properly.

When you mention 0.2V drop on the fuse was that measured on the bolts, cable lugs or exposed fuse blade. ab300A fuse should itself not have a high voltage drop or get hot at 150A. I am not sure you really have enough battery, again as you do not give your inverter model I can not confirm.

btw, there is nothing wrong with fuses, my 3000VA 12V Multiplus has run for years through a 400A fuse without issue as have most others.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

rvnomad avatar image rvnomad commented ·
It’s the MultiPlus II 2x120 3000VA


Any particular type of material for the washers? Copper or stainless steel or does it matter?

0 Likes 0 ·
pwfarnell avatar image pwfarnell rvnomad commented ·
Copper or brass, this is what Victron supply on their shunts. If you run the inverter at max load you a lot you might like to consider more battery capacity.
1 Like 1 ·
Show more comments
rvnomad avatar image rvnomad commented ·

@pwfarnell


What’s a good torque for these contacts? Battleborn suggests 10 ft-lbs for their battery terminals. Is that a good number for the fuse as well?
0 Likes 0 ·
pwfarnell avatar image pwfarnell rvnomad commented ·

I am metric but have checked US units, for M8 (5/16") 9ft.lb and for M10 (3/8") 15ft.lb are figures from Victron equipment (shunts / battery / inverter terminals)

1 Like 1 ·
rvnomad avatar image
rvnomad answered ·

@pwfarnell


So I replaced the Allen key bolts with hex bolts and washers and torqued them to about 10 ft lbs.

img-4842.jpeg


Result:

The cable lugs no longer heat up.

The ends of the fuse no longer heat up.

The very center of the fuse (where the yellow arrow is pointing) heats up to about 50 deg Celsius. Is this a cause for concern?

Voltage drop across the inverter is still about 1.1 volts when running the microwave at 150 amps.


Next steps:

Check voltage drop across the inverter cable lengths.

Any other suggestions?


img-4842.jpeg (502.1 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pwfarnell avatar image pwfarnell commented ·
A fuse is a resistor, when the current is high enough it has to melt so running a 300A fuse at 150A will generate some heat. The spec for 300A ANL is 0.35 milli ohm, so at 150A that is 8W so it will warm up a bit. I do not know the expected temperature but 50degC does not sound unreasonable.


Regarding next steps it is just a case of checking voltage drops with a multimeter and connections for temperature. A poor isolation switch is often the cause of voltage drop.

1 Like 1 ·
rvnomad avatar image
rvnomad answered ·

@pwfarnell : I replaced the long run of cables and saw a major improvement. I also replaced the fuse and made sure every connection had proper washers and torqued the nuts myself with a torque gauge.

Thanks very much for all your suggestions that helped me understand this much better!