question

fbo avatar image
fbo asked

Turning off MPPTs intentionally

Dear Victronians,

my setup is a GX, some Multiplus II and some Smartsolar MPPTs using ESS which avoids to feed power into the grid. I'd like to turn off the MPPTs from time to time to implement an upper SOC limit. This document

https://raw.githubusercontent.com/victronenergy/dbus_modbustcp/master/CCGX-Modbus-TCP-register-list.xlsx

shows a writable modbus variable ( "/Mode" , 774) which affects the MPPTs in the way I want. But: Is it safe to write to it often (is the state stored in a flash)?

Optimally, I'd like to set the MPPTs maximum charge current/power but there seems to be no way to do so. Is this correct?

Thank you for any advise.

Frank

ESSMPPT SmartSolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
andrii-podanenko avatar image
andrii-podanenko answered ·

It is safe

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fbo avatar image fbo commented ·

Hi Andrii,

thank you very much. Do you know of a source, where to find information like that? I'd love to make a map "modbus address" to "flash or not".

Best regards

Frank

0 Likes 0 ·
alexander-uhde avatar image
alexander-uhde answered ·

Hi Frank,

wouldn't it be better to use "max charge current" for that?
I have implemented a node-red function to restrict SOC to certain limits from time to time.

Using modbus this should be register 2705 for an ESS.
I guess this should be safe to be written often, since it seems to be used by ESS regularly when nearing certain SOC limits.


Regards

Alex


Edit:

"Optimally, I'd like to set the MPPTs maximum charge current/power"

Sorry, I did not read this one carefully enough the first time.

"max charge current" exactly does this one.

You can set it in 1A steps from zero to whatever maximum is possible.
This value can be overwritten by your BMS, if your desired value is higher than possible.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fbo avatar image fbo commented ·

Hi Alexander,

2705 seems to be a Victron setting which means, it's defined in /data/conf/settings.xml and updated there. Unfortunately, my use case requires frequent writes (e.g. once every 5 minutes) which is a bit much for my GX's flash storage

Best regards

Frank

0 Likes 0 ·
alexander-uhde avatar image alexander-uhde fbo commented ·

Hi Frank,


I am afraid I cannot give detailed advise on that.

In my use case I am shifting this value only 3-4 times a day during the summer and maybe 2 times a day during winter.

(I own a MP2 5000 GX with a MPPT250/100 and two additional SMA inverters connected to Ac-out).


Victron seems to use this in their own implementation of Venus OS large (Node red).

I checked the behaviour just some minutes ago. If I am changing the affected node in OS large, I can also see this change in register 2705 via modbus.

Normally I am not using modbus to communicate to victron, just using node-red.


Did you have a look at this already?
https://www.victronenergy.com/live/ess:ess_mode_2_and_3


Victron sugessts to use 2705 in this one as well, but unfortunately I could not find a statement for write cycles of the GX`s flash at all.