question

henrik avatar image
henrik asked

SmartShunt registering decreasing SOC even though battery is full

Having a problem with the Victron SmartShunt registering a constantly decreasing SOC even though the battery is at 100%. I have a 200Ah LifePO4 battery and a 450W panel with Victron SmartSolar regulator. Any idea what could be wrong? Could I have the wrong settings in SmartShunt? All minus cables go via SmartShunt.

(I have verified that the battery is mostly full. Good solar conditions are topping up the battery and it is not accepting more current. Built-in SOC in the battery shows 90-100%)


skjermbilde-2024-06-14-kl-092054.png


skjermbilde-2024-06-14-kl-091540.png

SmartShuntSOC
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
henrik avatar image
henrik answered ·

Also, here are my SmartSolar settings, if that's relevant. Is there anything I should do to debug this?


skjermbilde-2024-06-16-kl-120405.png


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image
klim8skeptic answered ·

@henrik With your Smart Shunt change the "charged voltage" to 14.0v.

Peukert exp to 1.05 for the moment also.

The shunt will then sync to 100% when the batt voltage is over 14v, with a charge current less than 8a, for a period of 3 mins.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

henrik avatar image henrik commented ·

Thanks! It was nice to get an explanation too :)

1 Like 1 ·
Show more comments

Related Resources