This will be better answered by the Victron staff...but.
yes, all models have it, but local regulations differ, and there is a limited number of country's where the products are validated for.
Some country's are ok with the normal Multi's / Quattro's, other demand dual relays in input of inverter, so there the Multigrid / Multiplus II is needed.
Country's that are not yet 'supported' need an external anti-islanding device unfortunately.
Normal MultiPlus No. Just Multiplus 2 and Multigrid have AntiIsland integratet
It depends on the definition of anti-islanding, more exactly local regulations.
Every multiplus is capable to cut internal inverter on grid failure
Normal MP has a LOM detection, but thats not my understanding of a requested full AntiIsland Protection like victron write in its produkt datasheet of MP2 or MG "With Anti-Islanding built in"
regards
Additional resources still need to be added for this topic