Why AC grid power in "dashboard" is different from values in "advanced" mode.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Why AC grid power in "dashboard" is different from values in "advanced" mode.
Reboot the GX. Or maybe first...
Check if cpu or d bus round trip are ok. Might be overloaded and cutting the real time connection.
Hi,
GX Reboot did not change anything.
AC VE Bus data in "advanced" view is way out of wack compared to GRID data in "dashboard" view.
At the same time data on the AC out is the same in dashboard and advanced views.
What I see now in "advanced" view, for AC in power values, does not make any sense.
In "dashboard" view all numbers are more or less logical. All power is accounted for.
AC out power values in "advanced" view are as they are in "dashboard" view.
There is no problem without PV production.
After observing the power flow in the system, I come to conclusion that "Grid" values are not the same as "AC in" in the VE Bus summary.
The VE Bus summary shows only the power on the input of the MP-II.
If there is a PV ON-grid inverter in front of the MP-II, the "Grid" would show the power fed into the grid from PV ON grid inverter and power from MP-II, if there is a surplus from other sources being fed to grid by MP-II.
Conclusion:
There is no problem with VRM data.