question

patrickvanneck avatar image
patrickvanneck asked

What is the AC rating for the relay of smart solar MPPT RS 450/100 and /200 ?

the spec sheet only mentions DC rating

Relay
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
nickdb avatar image
nickdb answered ·

It is a DC charger, why would it have an AC rating?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

deonkorb avatar image deonkorb commented ·
Because you might use the relay to switch an AC load, like a light?
0 Likes 0 ·
nickdb avatar image nickdb ♦♦ deonkorb commented ·

That is not its purpose, as far as I am aware.

From the manual:

Programmable relay which can be set for general alarm, DC under voltage or genset start/stop function. DC rating: 4A up to 35VDC and 1A up to 70VDC

0 Likes 0 ·
Show more comments
Alex Pescaru avatar image
Alex Pescaru answered ·

Hi @patrickvanneck

In other inverters, like MultiPlus II 48/5000, where they provide the same DC ratings, they are also saying the AC ratings.

So, it could be assumed that they are using the same type of relay in Multi RS and its ratings are the followings: AC rating: 230V / 4A, DC rating: 4A up to 35VDC and 1A up to 60VDC.

Which seems pertinent, because the flame extinguishing necessities for AC are more relaxed than in the case of DC.

Alex


1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

patrickvanneck avatar image patrickvanneck commented ·

Thanks Alex: this is really helpful.

I will use this to steer several 120V-coil power relays that will switch loads from inverter to grid and back depending on battery voltage, because in my country we cannot connect any solar to the grid at all.

1 Like 1 ·