question

tabet avatar image
tabet asked

quattro charging problem bsl battery

whatsapp-image-2024-05-14-at-203834-2edc3f7e.jpgwhatsapp-image-2024-05-14-at-203836-ebd006d7.jpgHello everyone,

I have a Quattro 15kVA connected to a BSL lithium battery in an AC coupled system. The Quattro is programmed to charge the batteries with 80A DC, but it isn't charging more than 20A. Additionally, the inverter shows that the batteries are at 95%, while the actual battery level is 29%.

the ess is putted keep battery charge.

How can I resolve this issue?

MultiPlus Quattro Inverter Chargerbattery chargingESSbsl
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
JohnC avatar image
JohnC answered ·
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

tabet avatar image tabet commented ·
yes all and i still have this problem there is a difference between battery soc and quattro reading soc


0 Likes 0 ·
Show more comments