question

fancourt avatar image
fancourt asked

Prevention of PV Potential Induced Degradation (PID) with Multi RS Solar/Inverter RS Smart Solar

I'm still learning about this topic and hoping for some assistance from those more knowledgeable in this area than me...

Given that the RS series solar charge controllers do not allow Earthing/Grounding of the PV DC conductors and that these SCC are designed for array voltages that apparently approach/exceed the voltage threshold where PID of PV arrays becomes an issue, is there anyone from Victron (or elsewhere) who can explain to me either:

1) how this issue is not applicable to these RS products or

2) how to prevent it occurring in systems using these RS products?

I would rather not have to resort to "Anti-PID boxes" that apply a large reverse potential to the array at night to attempt to 'undo' the PID effects caused during daylight operation.

The DC PV circuit on standalone MPPT RS controllers is obviously galvanically isolated from the battery connections, so it should not be possible for any potential between the array and earth/ground to exist.

However I have only just learned that there is NO galvanic isolation between the DC PV array circuit on Multi RS Solar and the AC output, so if the AC output is not configured as IT (ie any of TN-S, TN-C or TN-C-S or TT) then there will likely exist a potential between the PV DC and Earth/Ground.

There is no mention of this lack of galvanic isolation in the Inverter RS Smart Solar manual or datasheet (that I could find), but I am still waiting for confirmation whether the same lack of galvanic isolation as exists on the Multi RS Solar also exists here, but I suspect it does.
https://community.victronenergy.com/questions/289852/inverter-rs-smart-solar-galvanic-isolation.html

I'd be very grateful for any clarification anyone can provide.

mppt rsMulti RSinverter rsrs inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alex Pescaru avatar image
Alex Pescaru answered ·

Hi @fancourt

From my knowledge:

1. The PID is in fact a leakage current / positive ions generated by high DC voltages that move from the glass, frame and installation structure to the solar photovoltaic cell. But no one is forbidding you to ground the PV frame. And when grounding the frame, there is very little possibility of PID.

2. In general, PID effect is noticeable from 1000V strings and up. I doubt many will have more than 400V strings (most under 350V), this also because of the effect of the negative temperatures on string's VoC.

Just my 2 cents...

Alex

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fancourt avatar image fancourt commented ·

Regarding Point (1), see my reply to @Duivert NL below. Grounding the frame causes PID, not prevents it.

Regarding Point (2), there seems to be no consensus on the minimum voltage threshold at which PID occurs. Some sources say 600V, others say a lot less - for example the SMA document linked to below refers to MPPT ranges of 300 - 500V which overlaps very significantly with the range of array voltages connected to RS Series MPPT controllers. Unless you're installing in a climate that gets colder than maybe -10 C in Winter then your "most under 350V" comment is unlikely to be true.

A large proportion of Victron's global market would never see temperatures colder than -10 C and therefore I would suggest array Voc of >400V would be reasonably common in these climates. In the specific case I have in mind here Voc (@STC) is 410V and unless Climate Change dramatically messes with Winter minimum temps then this array should never, ever hit 450V.

1 Like 1 ·
Alex Pescaru avatar image Alex Pescaru fancourt commented ·

Hi @fancourt

I stand corrected. You may be right... Sorry.

What I can say is that the power output of my panels connected to the Multi RS Solar is in no way "reduced by up to 70%" how they are saying on those documents. The solar power curve is as it should be for the conditions. Sometimes even bigger than NOCT specifications.

But my panels are not grounded at all, despite safety rules, I know...

More of that, the PV panels are the cheapest thing from a solar system. And at 20 cents or less per watt and their longlife specifications, you can change them when you suspect "foul play".

Alex

1 Like 1 ·
Show more comments
Duivert NL avatar image Duivert NL commented ·
i agree with that, grounding the frame and installation brackets will prevent PID
0 Likes 0 ·
fancourt avatar image fancourt Duivert NL commented ·

Everything I have read precisely and completely contradicts this.

Assuming everything I have read isn't completely wrong, the cause of PID is actually the very fact that the PV module frames and brackets are grounded.

Grounding the frames allows a current to flow from the cells themselves to ground via the frame changing the properties of the cells and degrading their output.


https://pubs.rsc.org/en/content/articlelanding/2017/ee/c6ee02271e
https://files.sma.de/downloads/PID-TI-UEN113410.pdf
https://www.pv-diagnostics.com/blog/pid-reversal-process-for-on-site-pid
https://eepower.com/technical-articles/causes-and-solutions-of-the-potential-induced-degradation-effect-in-pv-modules/#

I could add many more links, but that should suffice I hope.


0 Likes 0 ·
Show more comments

Related Resources

Additional resources still need to be added for this topic


Inverter RS Product page.

Inverter RS Online Manual.

Inverter RS Datasheet.

Additional resources still need to be added for this topic

Mutli RS Solar Datasheet

Mutli RS Manual


MPPT RS Product Page

MPPT RS Datasheet  

MPPT RS Manual  

MPPT Error codes

MPPT RS Manual Error codes

MPPT RS Training Video