I have set up Mulitplus input #1 to ignore AC input using the general flag.

When I try to set up input #2 for input current limit control the setting for input #1 stops working, and the relay stays set to off. Why is the input current limit control causing the ignore AC input not to work


screenshot-2024-05-30-114918.png

Assistants
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alexandra avatar image
Alexandra answered ·

@PBdub

The relay control is very simple logic.

And relay on commands are prioritised over relay off commands.

What you may have to do is daisy chain two inputs on the inverter and have one condition on one and the other condition on the other that control the one action.

You are already using aux 1 and 2 you may have to use temp as well to do the third.