Victron Quattro 12/3000/120 turns off occasionally

Hi,


Ive had the Victron Quattro 12/3000/120 for about 3 years now. I bought it togehter with AGM batteries back then. Ive never had any issues.


I recently upgraded to LiFePO4 batteries and starting having an issue where suddenly at random without any warning or errors the 240 electricity goes off and when I look at the DMC all lights go off. This lasts for a couple of seconds and then everything turns on again like nothing ever happened. This happens like once or twice in a week. There is nothing specific that I suddenly turn on or off.


Any ideas what might be causing this?

Thanks in advance.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
snoobler avatar image
snoobler answered ·

Some LFP batteries behave erratically if single cell over-voltage protection (OVP) is triggered. It's very common for new LFP batteries to have imbalanced cells where one cell hits peak voltage before the others. This triggers over-voltage protection.

Try reducing your absorption voltage to 13.8V with a 2 hour absorption period. This should still allow you to get fully charged, but it should reduce/eliminate any OVP events.


4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lennon avatar image lennon commented ·
Hi Snoobler,


Thanks so much for your quick reply! that sounds logical indeed. The LFP manufacturer stated absorbtion volt should be at 14.4. Should i lower that all the way to 13.8 then?


Thanks!

0 Likes 0 ·
Show more comments