Probably a fairly straight forward question to answer, but just starting out with Victron equipment.
Designing a system with a 10kva Quattro and 4 x Pylontech US5000 batteries.
The supplied cable is 25mm rated at around 120A, with each battery claiming a max continous power output of 100A each.
They're sort of designed to be daisy chained, but I soon noticed that's going to be an issue as I'm guessing 4 x batteries daisy chained could output 400A max continous? Is that about right?
In that case, what is everyone doing with their Pylontech batteries, are you making custom 50/70/95mm cables and daisy chaining them in pairs or more, or are you just wiring each battery back to the distributer with its own 100/125A mega fuse?
Other quick question, I'm guessing if they all are wired individually, I can still daisy chain the comms cabling to just send one bms cable back to the Cerbo?
Appreciate your time answering in advance,