Now, here’s something that makes me wonder:
I’ve been drawing up to 7 kWh from my Victron twin Multi 5k and 20k battery storage with no problems for months now and the only item that will cause a system cut-off is my larger Hydrovane Compressor out of two.
The smaller one’s motor is rated 1.1kWh and never gave me problems even when I only had one Multiplus installed and, tested yesterday, it draws 16A as rush current and 8.5 A once running.
The larger motor is rated 2.2kWh and draws 25A at start and 17 A in normal operation.
When I only had a 5K battery and one Multiplus it would not even start without halting the system, not even with a soft start installed however now with 20k storage and two Multi in parallel, it only runs for about 40 seconds before the same problem occurs shutting down the main relay.
How can that be? The readings don’t lie and if it takes 25A to start with no problems why should it halt the system with only 17A after a short period of time?
It runs perfectly from the grid.
I get the typical message “L1 Overload” & “Battery low” but when I check the voltage in VRM it is never outside the normal range.
All cables are of the correct size, 50mm for the 5k battery and 70mm for the 15k, 70mm for both Multi and 30mm for the two MPPTs.
No loose connections or battery busbars, the larger battery has an 180A Eaton fuse.
Lynx shunt and distributor Multiplus fuses are genuine Victron 325 & 200A and I have installed auxiliary generic 100 + 200A Mega fuses in the Power In which are the only unknown quantity.
My question is, within the complex mixture of settings amongst Links, Battery, Multi etc. . . have I missed one that could cause this major problem?
The images show only - 11.3A and -18A at the time of the tests with a steady voltage of around 55/56 v at the VE bus.