I installed a Victron MultiPlus II 12/3000/120-50 2x120V in my trailer to charge 400AH of LiFePO3 batteries. When I plug everything in and try to charge the GFCI circuit faults. I've tried 3 different GFCI circuits.
- With the MultiPlus off, there is no ground fault and I have AC power from the same GFCI outlets.
- As soon as I turn on the MultiPlus, the power light blinks, steadies, then I hear a relay click as it tries to charge. GFCI faults immediately
- The input current matches the outlet, it is not blowing the breaker on the curcuit.
- It happens with all AC output from the inverter off (downstream breakers).
- I configured the Inverter's ground relay to 'off', made no difference.
- It works normally from a non-GFCI outlet, and from my Honda EU2000i generator.
I can't find enough information from Victron to understand what the ground relay checkbox does from an elecrical standpoint to know if unchecking it should have made a difference. Not sure whether to return this unit as defective and get another one or if I will have the same problem. My dealer says they don't know enough to even have a conversation with victron about this and, in their experience, victron won't talk to customers. Anyone have any insight into this issue?