Hi,
Im missing a couple of thousand watts on the grid side...
No limit active!
Any idea? (no there are no hidden/invisible consuming devices)
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hi,
Im missing a couple of thousand watts on the grid side...
No limit active!
Any idea? (no there are no hidden/invisible consuming devices)
Yep, that is odd... Assuming it isn't a metering issue the only other explanation I can think of is poor power factor somewhere, that is a stretch to be fair as it would need to be down at 0.75 ish.. The grid seems to be circa 0.98 / 0.99 so that only leaves a load taking a big chunk of reactive power...
Can you get current real time measurement's for the AC load? (and preferably the AC coupled solar too) I will be following to see how this one shakes out...
In the meantime I've ckecked the voltages on both sides (tracker and Inverter)
-> both are the same value so thats ok
Furthermore I saw that this occurs only when we are on high production.
e.g. when production is at 20.000w there is almost no problem, now at over 30.000 I'm missing a few thousand watts of output to the grid again.