My ESS system isn't working properly. Firstly the SOC readings are all over the place, at the moment the voltage (from the BMS says 51.8v and it displays as 99%). When it charges the SOC leaps from wherever it is immediately to 100% and then doesn't display properly. It will never discharge below 70-75% despite the limit being set for 20. The problem then is as soon as the LOW BATTERY alarm goes if forces a charge, usually when the electricity prices are high, which negates the point of having the system entirely. I'm not at home so I can't interrogate the BMS (Pace, I think, on a Fogstar 15.4kWh battery) but from what I can see it's the Multiplus forcing the charge not the BMS as the BMS isn't showing any alarms. Thanks.
PS. It's a Multiplus 8000 on v5.10. We have a small amount of solar which produces around 5kWh a day, the battery has a BMS with a 'Victron' setting, and the Multiplus is wired in 'single leg' to the grid. Cerbos S is up-to-date. We are on a dynamic tariff (Octopus Agile Roll on DESS support!) and so far I've ben manually setting charge periods. Mode: Optimised WITHOUT battery life.