Every time my battery soc reaches 100% I get high voltage alarms 512. Off grid SolarEdge se17k inverter connected to 3 Quattros 48/10000 charging to BYD battery boxes, Cerbo GX etc.
Any solutions or settings to adjust?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Every time my battery soc reaches 100% I get high voltage alarms 512. Off grid SolarEdge se17k inverter connected to 3 Quattros 48/10000 charging to BYD battery boxes, Cerbo GX etc.
Any solutions or settings to adjust?
If you have followed the online manual for set up then you should be fine.
If you look a bit closer it is actually a warning alarm not an alarm alarm.
The BYDs will have dropped the CCL down and been taking care of it.
Load up the bms min and max cell values you will see a deviation there.
There is a section that is in the manual dealing specifically with this behaviour in BYD batteries. There is potentially one temporary tweak to get them to calm down.
I see one of the solutions is to run the generator to keep the batteries at 100% in order to balance them quicker. Currently, the gen is set to shut off when soc reaches 75%. What's the best way to adjust the settings to have the gen keep the batteries charged until they are balanced?
MultiPlus Product page / Quattro Product page
MultiPlus 230V Manual / Quattro 230V Manual
MultiPlus 230V Datasheet / Quattro 230V Datasheet
VE.Bus Error codes / VE.Bus configuration guide