question

chris-wren avatar image
chris-wren asked

I have Phoenix Multi-Plus 24v 3000VA 70amp unit and Skylla-TG 24 100 on the SAME batteries! Surely this is wrong?

battery charging
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

It’s a lot of charge current potential, but not necessarily wrong?

Sometimes this configuration is advised if you need to isolate a very bad grid. The skylla can take a terrible grid voltage, use it effectively while the multi supplies nice clean power to the loads.

Then generator is connected to the multi for the power assist features.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image
JohnC answered ·

Hi Chris. It's certainly a lot of charge capacity, unless you have a very large batt bank. Have you 'inherited' this system? Both have ways to limit their max charge current, then the batts will likely self-limit anyway, so they can't push beyond what the batts (and concurrent loads) can accept.

Maybe tell us more about your system, and your concerns..

Edit/: Crossed with Guy, but I'll leave it anyway.