Hie,
I have a Multiplus 2 connected to a Victron battery (70Ah). The system shuts down after bulk charging as soon as it is about to go into absorption.
Please help
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Hie,
I have a Multiplus 2 connected to a Victron battery (70Ah). The system shuts down after bulk charging as soon as it is about to go into absorption.
Please help
Hi @DELTAPOWER
I think this is due to your battery being much to small for the system, is this the 'Mr. Crossley' site?
I see big spikes in DC voltage, and high DC-ripple alarms.
Thanks for your prompt reply.
Was wondering though; the batteries are 4.8kWh 48V, so maybe my capacity is 100Ah instead of 70Ah as previously mentioned.
Is this still too small for a 5kVA Multiplus II?
If so what is the minimum battery bank capacity for the 5kVA system?
Hi @DELTAPOWER
Not what you want to hear but 'it depends'
Exactly what batteries do you have?
I'd first set the charge voltages a bit lower and see if that fixes your problem.
Try: absorbtion 56 volt, float 55 volt.
And another remark: Please check your battery wiring for bad connections, you have a battery voltage that fluctuates too much. Hence the 'high DC-ripple' warnings.