PV power to the battery/consamption from the battery

Hello guys!

I have three-phase ve bus system with two PV chargers.

I think I have some problem with in/out power calculation on VRM portal.

If I take one-day data from VRM its look like the PV to battery power more than the battery to consumption power. So how it's happening? If I take from battery less then I use where the excess power is going?


VRMchargerSolar Panelpowerassist
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Daniël Boekel (Victron Energy Staff) avatar image
Daniël Boekel (Victron Energy Staff) answered ·

Hi @Alperin

A number of reasons:

-battery efficiency (charge / discharge, peukert, etc) + charger / inverter efficiency

-it can be that you use some of the energy the day after the charging has happened (and / or the other way round)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

embtek-solar avatar image
embtek-solar answered ·

I have a similar Problem with the efficency of the battery. I want to share two examples with you and hope for an explanation.

Example A: DC coupled PV; 2xPylontech US5000; 3Phase MP2 setup

  • PV -> Battery: 4.6kW
  • Battery -> Consumption: 3.6kW
  • More than 20% lost


Example B: MP2 + 1xPytes 5,12kWh Battery; AC-Coupled (small system)

  • PV-> Battery: 3,8kWh
  • Battery -> Consumption: 3,0kWh
  • More than 20% lost

Is there sth I do not understand or have wrong configured? :)


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

Sounds about normal for pylontec. They are not as efficient as they make out.

The reabsorption cycle also affects efficiency.

Further comment lower voltage batteries tend to be a bit more inefficient.

0 Likes 0 ·