Is it possible to use Energy Meter VM-3P75CT in a 3 phase 3-wire system?. This is the most common system for households in Norway. I can't find any wiring diagram without N in the manual
My supplier couldn't answer
Thanks
Arvid
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Is it possible to use Energy Meter VM-3P75CT in a 3 phase 3-wire system?. This is the most common system for households in Norway. I can't find any wiring diagram without N in the manual
My supplier couldn't answer
Thanks
Arvid
Hi @Arvid ,
No this is not possible with the VM-3P75CT. Some of the other meters such as EM540 do support 3-phase 3-wire system.
Such a meter hasn't been announced yet. If you need a 3-wire energy meter with CTs, you can use the EM530 (specifically the EM530DINAV53XS1X). Victron doesn't stock that meter, but it is compatible with the Victron ecosystem. You can also take a look at the Energy Meter Selection Guide for other compatible meters.