Guimods not recognizing that generator is running.

@kwindrem, I hope that my problem is easily solved by pointing out what I am missing. I had to replace my Cerbo GX and I am now running v3.31. I downloaded the latest Guimods package manager and installed.

When I run the generator, the system does not recognize that the generator is running. I am using the Cerbo Digital input #1 set to generator and when the generator is running, that signal reports that the generator is running. But the main display says that power is coming from the grid and I do not get the generator input current limit page.

I know that the ExtTransfer switch functionality was changed. Where or how do I get Guimods to recognize that the generator is running and switch to an input limit that matches my generator?

Any help greatly appreciated.

Generator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
derrick thomas avatar image
derrick thomas answered ·

The exttransferswitch function requires a second digital input be set to 'external transfer switch' mode, and a relay be installed that will trigger that digital input from the ATS when the input switches between shore/grid and generator.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnjaymack avatar image
johnjaymack answered ·

@derrick thomas, I am running v3.31 software. The extternaltransfer switch package says that it is invalid in v3.31.

I found out what I did wrong and your suggestion actually lead me to the answer. I had digital input #1 set to generator. I went back to that setting and checked and found that when I installed Guimods, I guess, an external transfer switch option appeared. When I checked that box, I now have a line in the device list menu that reads External Transfer Switch.

I am sure that the information regarding setting the digital input from generator to external transfer switch is in the Readme files, but I sure missed it. In any event, my system is working and all is good.

As a matter of interest, I had implemented the cooldown functionality using a couple of relays and Assistant programming on the inverters. It worked like a champ until I was forced to update the Cerbo software. Since the new software had the cooldown function apparently emplimated, I removed my relay work around. I was told that my current, at the time, inverter software should implement the new cooldown functionality. That advice was incorrect.

I read somewhere that Guimods maybe going away. If that is correct, I will miss it. I have found the displays to be much more intuitive that what I have seen, so far, in the Victron stock. Also, my wife understands the Guimod displays much better than the stock displays.

Also, the ease of changing input current limits, and the automatic changing of input current limits from current grid-to-generator and then back to grid something that I have not heard that Victron is working on. I use that feature regularly since my grid/shore power input limit change regularly as I travel. Once again, my wife found it easy to remember to tap the grid icon, tap the required new input power setting, and be done with it.

Since I am not a true programmer, I can only guess at how hard it is to implement new, stable, features. I look forward to what many more months will bring.

In any event, thanks again for the help. It is greatly appreciated.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

derrick thomas avatar image derrick thomas commented ·
With v3.31 exttransferswitch is included in guimods, but you should still be using 2 digital inputs. Digital input 1 should be enabled as the generator run signal as described in the victron manual to tell the gx that the generator is running, and a second digital input triggers the exttransferswitch logic that the generator is putting out AC power. Although exttransferswitch is now included in guimods, the setup and operation is still the same.
0 Likes 0 ·
johnjaymack avatar image
johnjaymack answered ·

OK, I am confused @derrick thomas. I tested and it appeared to run with only one signal. I will accept that it needs two, but I wonder why? The generator warm up, cooldown, and stop timers should only come into play if the Cerbo knows that the generator is running. And the timers did work. I will test again tomorrow. Just to be sure. I don't mind putting in the second signal, but I am curious.

Also, can I jump the two digital inputs together since I only have one set of signal wires? I have three unused digital inputs so using a second input is not an issue. If I can use the same set of wires to both inputs, then the change is simple. Any thoughts?

Thanks


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

derrick thomas avatar image
derrick thomas answered ·

If you are using relay 1 for auto start functionality you should have a digital input set to 'generator'. I suppose you could use the same signal for a second digital input set to 'exttrasferswitch' but that is not the preferred method. There is the possibility of a situation where the generator is running but not supplying ac power. Having a digital input dedicated to exttransferswitch that is triggered from the ATS ensures that the generator ac input current limit is only selected by the GX if ac power is detected from the generator. This is easily achieved by triggering a relay from the generator side of the ATS which toggles the digital input that has been set to 'exttransferswitch'. The 2 digital inputs serve different purposes and should be fed from the appropriate sources.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

johnjaymack avatar image
johnjaymack answered ·

OK. Thank you @derrick thomas for the explanation. It makes sense. In my situation, if the generator runs, the ATS disconnects shore power and connects the generator. I cannot run the generator without disconnecting shore power.

I will add the second digital input.

Thanks for the explanation.