CL 12/100 Throttling at 65% SoC on 10kw bank

I have my CL 12/100 connect to CCP2 (175A) in my Ford Transit with Dual 250A alternators, i've pulled 160a off it many times before. The van is putting out 14.2v - 14.3v consistently.

I'm using the renewable settings on my multiplus, with it set to stop charging at 13.3v, to give my solar panels and alternator space so i don't waste "free" power. My 10kw bank it usually has 2kw of space for solar/driving.

The problem is i can get down to 65% and be at 13.3v if i don't have any heavy loads. But it seems my CL12 starts to throttle when it sees above 13.3v, it drops the output current % and i'm only getting ~800w, or if it see 13.5v it drops to ~600w. If my solar panels are putting out 300w or more it throttles even more.

If i put a heavy load on the batteries that drops the voltage, it will jump back to 100% which is ~90A/1.2kw. Never seen higher than that.

Is there any way i can disable the throttling on the CL12?

battery chargingBMSbattery system voltagecharge current limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
badwolf avatar image
badwolf answered ·

Went for a drive, it cloudy today and this is what im seeing.

img-2566.pngimg-2565.png



img-2566.png (386.5 KiB)
img-2565.png (305.8 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image
klim8skeptic answered ·

@BadWolf Is there any way i can disable the throttling on the CL12?

Battery current limiting is the function of the battery output fuse . A 125a fuse gives the max current output of 100a.

The input voltage (13.9v) to the BMS is a bit lower than the alternator (14.2). The higher the input voltage to the BMS, the higher the charge current will be.

Check your alternator to BMS cable, and the battery to ground cables are rated to reduce the voltage drop.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

badwolf avatar image badwolf commented ·

I have it set for 100a output, with a victron 125a 58v fuse. I had the 32v version and just recently swapped to the 58v. I did see a charge current % improvement of about 10% with the 58v.

What i'm trying to prevent is the Charge Current % from dropping, it was at 82% in the photo above.

When i used the 100A fuse(that came with it) with the default 90A output max was 75A @ 100% current

When i use a 125A 58v fuse with the 100A output max is ~90A @100% current (was 85A with the 32v)

Using my Klein Volt Meter

When i turn on the CL12 the voltage output on ccp2 drops ~0.1v,(expected) and i'm seeing it at the end of the cable run (4ft 1/0 cu) on the terminal of the CL12. But the CL12 is reports 0.2v lower than that reading.

The fused side that is charging the house batteries shows 0.15v higher than the batteries when charging as well.

If i move the CL12 Ground to the starter battery it does eliminate the 0.2v drop to on the Starter reading but then adds it to the Battery Voltage.

0 Likes 0 ·
klim8skeptic avatar image klim8skeptic ♦ badwolf commented ·

@BadWolf If i move the CL12 Ground to the starter battery it does eliminate the 0.2v drop to on the Starter reading but then adds it to the Battery Voltage.

Given that information you have a 0.2v drop on your negative wiring. Also note that the Gnd for the CL12 has to originate via the Neg post of the battery being charged by the BMS to be accurate.

Further to that, any voltage measurements need to be taken from the BMS Gnd terminal. You can even measure the voltage difference between the BMS Gnd terminal and vehicle ground.

0 Likes 0 ·
Show more comments