We are facing a issue that is mentioned a few times somewhere in the internet but i can't find a real solution for that.
We have 3 Quattro 8000/48 connected to 8 Pylontech US3000c batteries.
But when turning on the system from the battery (no PV, and no AC in available) the battery starts to turn on and goes straight in a alarm state and turns off again.
I've connected a fluke oscilloscope to see what the voltage and currents are doing:
First, the batteries do not turn on simultaineously but one after the other, meaning that all startup current is pulled only from the master battery.
The battery does a soft start, meaning the voltage goes up from 0 to 48v in about 3 seconds slowly.
However when i connect the inverters, the voltage raises to about 3v the current spikes to more that my meter can measure ( >250A) then the voltage goes immediately back to 0 and the battery is in alarm state.
This is a classic capacitor issue and could be solved with a resistor and a delayed contact bypassing the resistor after the bus voltage is slowly charged.
But it's this really the only solution? How is it possible that there are so many setups like this out there and no one else is struggling with that problem?
Thanks for advice