question

Michael Connolly avatar image
Michael Connolly asked

Generator startup from BMV-712 or SmartSolar 100/30?

Hi all

Does anyone know if either the 712 or the mppt 100/30 have the capability of starting a generator on an alarm activation?

Thanks

Mickc

MPPT ControllersBMV Battery Monitor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Peter Polz avatar image
Peter Polz answered ·

Easyiest way is with BMV. Maxiumratings of that BMV realy are 60V / 1A


You also can do it with SmartSolar and a Digital TX Cabel combined with a SolidStateRelay

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Michael Connolly avatar image Michael Connolly commented ·

Fantastic, I have s three point Onan genset and your attachment is spot I. For that...well done, kudos!!

0 Likes 0 ·