question

John Mitchell avatar image
John Mitchell asked

Can Victron ESS use a 3rd party energy meter

I haven't had my Multiplus II installed yet but I'm keen to use ESS. I already have Myenergi products installed so my grid consumption is already monitored. Do I need to install a Victron energy meter or can I pull the data from the Myenergi API? I hate having too much redundancy in my meter box and it will be an expensive install being 3 phase.

ESSEnergy Meter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @John Mitchell,

The Victron system supports some 3rd party energy meters, specifically some models of ABB and Carlo Gavazzi.

I have never heard of myenergi being supported, so I am quite sure they are not, but I can't say 100%.

For a bit more information check out this Energy Meter selection guide

https://www.victronenergy.com/upload/documents/Datasheet-Energy-Meters-Selection-Guide-EN.pdf

In almost all cases now I would choose to use the Victron brand energy meter, the performance of the integration is significantly improved.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

John Mitchell avatar image
John Mitchell answered ·

Thanks Guy - quick follow up - on the meters table it says for the CT clamp version a max of 5 amps per phase? I assume that is not the maximum of current it can measure but rather the max it can take via induction?

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @John Mitchell,

I am not sure.

The way I read that is the maximum it can measure, it can probably take more via induction, but I don't know how much or for how long, and I would be certain it couldn't read it (i.e showing 5A when there is 6A flowing).

In most cases I would size a unit that had a maximum current rating greater than the expected operating currents, and ideally on a circuit that is fused with a value less than the maximum.


The following is made up off the top of my head and shouldn't be considered accurate without further confirmation

The way that I understand how these analogue to digital CT meters work is that there is a voltage that induced by the current. The higher the current the higher the induced voltage, between a range of 0 and 3.3V or 0 and 5V.

Then there is some circuit in there that has some resolution of bits, say 4096 steps. So 0V is interpreted and 0 A, and 5V is interpreted as the maximum, in this case 5A. And everything else in-between 2.51V = 2.51A

That circuit that is reading the voltage has its own limits, those are not documented in the manual beyond the 'maximum', as a rule of thumb I would say over 10% is potentially damaging the measuring circuit, but it could be higher or lower for all I actually know.

0 Likes 0 ·
Duivert NL avatar image Duivert NL commented ·

hi, yes the 5A is correct for that type of meter, maximum current measure of 5A per Phase


if you need an fast meter with CT i suggest the VM-3P75CT

otherwise the EM 540, the slower EM340 or the slowest EM24 direct shunt version

0 Likes 0 ·
Show more comments
Duivert NL avatar image
Duivert NL answered ·

that could be possible!, i never opened one, but what i mean is there are different em24 versions

versions with internal measuring and versions with external CT clamps, CT clamp version is max 5A

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.