I have 12 Quattro II 15000 connected in 3 phase giving 180kVA and 360kVA short time rated. The Modbus registers are either +-32000 or 64000 for power readings. This is 5 or 10 times smaller than the values I need to see. As my load grows past Each multiple of this limit (say 64000) the most significant bit is dropped and my reading is back at zero. So when I am at 63999 W then my Modbus value is the same but when I reach 64001 W the Modbus value is 1 - the register has dropped the highest bit… has anyone found a way around this because I see no Victron plan to fix it after all these years ….?