question

davidtudor avatar image
davidtudor asked

Charging 3 Phase Multipluss ii

Hi,

I have 6 x Multipluss ii 5000KVA on a 3 phase off grid system with 27 solar panels and 3 phase 21KVA generator, when the generator is running at full load we get around 18kw from it and it will run a 10kw house usage and also charge the batteries around 100amp, i have 10 Pylontech batteries mixture of US5000, US3000, US2000. total of around 35KWH.

When no load is on the AC and the generator can use full power to charge the batteries via the Multipluss ii, i am only getting maximum 250 amp charge, 3 of the Multiplus are slaves, and i suspect they don't charge? Otherwise i am thinking the total rate of all six charging would be 6x70 420amp charge? Is this right? i know the batteries will take it as the Pylontech say they will take 500amp charge and i know i have had a 400amp discharge when our car is charging, via invertors and batteries.

Multiplus-IIPylontech3 phasecharge current limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Duivert NL avatar image
Duivert NL answered ·

hi what do you mean with 3 are slave?

If the pylontech’s are correctly wired and setup, the bms controls the maximum charge rate not the multi’s

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

davidtudor avatar image davidtudor commented ·
Yes the BMS pylontech controls the charge, but why is it so low?
0 Likes 0 ·
Duivert NL avatar image Duivert NL davidtudor commented ·
Maybe it depends on the SOC, i have 3x us5000 and they charge with about 40-50 amps max on 3 phase multiplus 2 3k at a 50-40% SOC while the mps can deliver a max of 105A
0 Likes 0 ·
davidtudor avatar image davidtudor Duivert NL commented ·
Probably mine is OK the at 250amp charge
0 Likes 0 ·
davidtudor avatar image
davidtudor answered ·

Hi

3 of the Multipluss are classed as slaves.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@davidtudor

Did you leave them at 70A on the MP2 default in settings when programming.

Confirm you do not have ESS assistant loaded?

Is weak AC enabled?

Do you have a GX? Confirm the Charge current is not capped in DVCC.

Is the input current limit up where it should be?

Validate your some inverters are not contributing to the charging theory with a DC clamp meter to check them.

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

davidtudor avatar image davidtudor commented ·
HI

I have no ESS, weak AC is enabled, i have a GX. I need to check other settings.

0 Likes 0 ·
davidtudor avatar image davidtudor davidtudor commented ·

dvcc.png

DVCC

0 Likes 0 ·
dvcc.png (32.6 KiB)
Show more comments
davidtudor avatar image davidtudor davidtudor commented ·

parameters.png

Parameters

0 Likes 0 ·
parameters.png (36.3 KiB)
Show more comments