The peak power of the Multiplus 2 5000, is stated as 9kW. Is that just from the inverter (not including any grid contribution)? What is the duration of that specified peak delivery? Thanks.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
The peak power of the Multiplus 2 5000, is stated as 9kW. Is that just from the inverter (not including any grid contribution)? What is the duration of that specified peak delivery? Thanks.
Hi @MattFR,
It depends on temperature, battery voltage, and AC output voltage.
For more insight into what an inverter overload is, and how it is triggered there is a detailed training available here - https://www.youtube.com/watch?v=4SXtGIx0x5w
Here is a little teaser about some of those details:
9kW is without context because the context is installation related which is extremely variable.
How long it is sustained (and if the system even can do it) is hugely affected by that.
The overloads are pretty much the same across all the equipment.
No system should be sized using the peak. It is there for 'mistakes' and maybe large short peak start draws which settle to nominal quickly, such as pumps and motors.
As you’ll see by the training video, there is only so much space available on the datasheets for what can be a quite a detailed explanation depending on lots of variables including the load itself.
None of the peak or surge values should be considered sustained in any sense. They are overloads, and permitting them makes the unit a lot more reliable (because loads often spike up on startup, or multiple simultaneously inrushing), but really should not be depended on for any length of time in normal operation.
The only value that should be considered sustained is 4000W into resistive load with power factor of 1, at a controlled ambient temperature of 25 degrees, with maximum airflow around the unit. That should be rock solid.
Other than that there is a huge variability in peak, especially on very very short time frames (1/50th of a second) up to the maximum current output of 50A, around where other protections such as the short circuit output protection are engaged.
I am sure the bigger numbers are used for marketing, but given the otherwise freely publicly available in depth resources available (here is another good one once you have finished the overload training) I don't think we are being disingenuous in any of the info provided.