Good day to all .
I need help with a very strange problem when trying to connect an Easysolar 48/3000/35 with a BSL 48-200PW .
I am a Victron , Pylontech and BSL distributor and installer , so very familiar with Victron / BSL integration . Did many of these .
The funny part is that this one is at my home !
I have an Easysolar 48/3000/35 - 240v (The old one, with the color control and the AC breakers at the bottom - See picture), since a few years . Had 4 batteries AGM 12v/200Ah and they are becoming old . Decided to replace these by one BSL 48-200 Powerwall .
Each time I try to connect the battery to the inverter, the battery goes on alarm mode and shuts down .
Please note :
- I first updated all the firmwares
- The BSL was installed at our lab with a Multiplus II 48-5000
- When I tried to connect and got the alarm , I tried many things .
- I brought a Cerbo and connected to the BSL . Works fine . I can see the BSL on the device list
- I added a MPPT 150/60 with a few panels to check charge . Charging perfectly .
- Today , I connected a separate Multiplus II 48/3000 . All fine and all working well together .
As soon as I try to connect the BSL to my easysolar, ... ALARM
- I first disconnected my color control, and wired it alone to the BSL (After having changed the settings) . All fine and BSL appears as normal on the device list .
I was thinking the problem could come from residual "inside connections/current " from the ancilary elements of the Easysolar , so
- I disconnected the integrated 150/70 and the color control
- I even disconnected the AC IN and AC out wiring
Same problem
I am a bit lost . Hope someone on this forum has already faced a similar situation and may have found the solution !
Thanks in advance .