question

jonatanjensen avatar image
jonatanjensen asked

AC out Voltage jumping while inverting in offgrid setup which is powering a house.

Quattro 10000, Fronius primo 8.2-1, 3 Mppt's 250/100, BYD LVL 600Ah

System is set up to 240V but output jumps between 230 to 250. Found it because lights started flickering more and more.

It's like related with tv and pc but not always happening only couple of times in a day.

screenshot1.png

It has been working fine since 2020.

Made firmware updates but still the same output.

screenshot-2024-03-31-104420.png


MultiPlus Quattro Inverter Chargervoltageacoutac out
10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
Is the inverter throttling the fronius at all?

What assistant do you have to control the fronius?

0 Likes 0 ·
Show more comments
Paul B avatar image Paul B commented ·

whats the DC voltage doing at the same time as the AC voltage goes Hi

maybe the a cell is going hi or LOW and the battery BMS is going open circuit and thus you may get a AC voltage spike before the hz increases.

if you turn the Fronius primo OFF does it still happen (ie does it happen during daylight hrs only ????

is something else coming online or disconnecting ie the generator

these are just some areas to look at.

0 Likes 0 ·
Show more comments
jonatanjensen avatar image jonatanjensen commented ·

Any advice?

0 Likes 0 ·
Show more comments
1 Answer
jonatanjensen avatar image
jonatanjensen answered ·

It looks like the reason was still the last update from fronius, sometimes it worked fine but it had some disabilities.

Support made a downgrade of the firmware.

Now it's been working three days like a charm, hope that's solved now :)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.