Hi there, I noticed when I updated to v506 on my MP2's I started to see my AC coupled PV being limited. So I did some looking and it was the frequency settings; however I need some help confirm what is the correct settings for my usage. It's worth mentioning that I do have DC PC aswell.
I'm based in the UK, and my system is Off-grid during peak hours 06:00 to 00:00 then the relays switch on and connect to mains grid. I'm running my MP2's at 245v
Looking at the settings of my MP2's:
Under Assistants:
Solar converter start reducing its output power at 50.20hz
Outpower Power will be reduced to minimum when frequency is 52.70hz
Converter will disconnect when frequency higher than 53hz
Under G99 Grid Code
U/V = 184v
OV stage 1 = 262.2v
OV stage 2 = 273.7v
U/F stage 1 = 47hz
U/F stage 2 = 52hz
O/F = 52hz
Solis 5G inverter settings:
U/V Stage 1 = 187v
U/V Stage 2 = 173v
OV Stage 1 = 260v
OV Stage 2 = 265v
OV Freq stage 1 = 52.6hz
OV Freq stage 1 = 53hz
UV Freq Stage 1 = 48hz
UV Freq Stage 2 = 47hz
Basically, I want to limit any AC PV clipping to start as late as possible and shutdown as last resort.
What I have noticed is that my Frequency (regardless of battery level) can be as high as 52.6hz; the frequency does move around a lot.
I'm not sure why the frequency move a lot as it doesn't seem to be to do with load or battery level.