question

blindbadger avatar image
blindbadger asked

Multiplus Relays - power from pos terminal stud?

I'm looking to wire up auxiliary PC fans for my multiplus to help provide it fresh air and was thinking about using the K1 relay connections for them

For the relays, I understand that a common way to wire them is:
- COMM from battery positive (with an inline fuse)
- NO to load (negative on load to battery negative)

Is there a reason not to get the positive connection from the battery stud on the MP? Or is it better to run the longer wire to go back to my distributor (my multiplus is mounted about 10ft away from the battery and loads bus bars).

Multiplus-IIRelay
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
delf67 avatar image
delf67 answered ·

The relay wiring you describe refers to "volt free" contacts. I'm not sure that's how the K1 terminals are used. They are labelled + & - (not Com/ NO) and are described in the manual as:

1. 12V 100mA

2. Programmable contact K1 open collector 70V 100mA (whatever that means).

The alarm relay is regular volt-free contacts (Com/ NO/ NC), so you might be better off using that.

As to your actual question; I can't see any reason you shouldn't power the fans from the battery studs on the MP.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blindbadger avatar image blindbadger commented ·

I'm running a Multiplus 1 24/3000-70, so maybe it's different on the MP2? My K1 is definitely a NC/NO/COM setup of terminals.

tempimage4qopig.gif

The "Primary Relay"/Alarm Relay is up near the top and much bigger, so I could use that too. K1 is just a bit easier to get to and route wires to.

I have Aux ports that's +/- (over left of the negative battery cable) but my understanding is that is more for switches. For that, would it still be 12v if the inverter is configured for a 24v battery?

Also, please forgive the small cables on the inverter...it's connected to a temporary battery and the limits are set low to accommodate the smaller cables until I finish the battery bay with proper 2/0 (hopefully tomorrow).

0 Likes 0 ·
Show more comments
kevgermany avatar image
kevgermany answered ·

The stud will be at battery voltage. Not good for 12V pc fans.

Relay specs are in the notes of the technical specification section of your manual, I think it's 240V, 4A, but can't be sure.

There's a good fan in the multiplus. Do you need another? Ensuring good air flow to and from it should be enough.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

delf67 avatar image delf67 commented ·
He could run 2x 12V fans in series.
1 Like 1 ·
kevgermany avatar image kevgermany ♦♦ delf67 commented ·
Or a buck converter
0 Likes 0 ·
blindbadger avatar image blindbadger delf67 commented ·
Yeah, series was my plan for the fans. The multiplus is mounted on its back due to space constraints so I wanted the fans to help keep fresh air flowing through it to help.
0 Likes 0 ·
kevgermany avatar image kevgermany ♦♦ blindbadger commented ·
I think you'll find it blows out at the top, so good ventilation at the bottom and extraction at the other end.
1 Like 1 ·