Hi,
I'Ve installed the Venus version 3.30 and also updated the ESS assistant to the recent version. Unfortunately when activating peak shaving export limit it does not work. It will throttle my Fronius 10kW inverter permanently.
I've an old Solutronic inverter (4.5kW) connected to AC in which can't be throttled. On AC out sits the Fronius inverter connected via Modbus. Additionally I've an MPPT connect on the DC side and a Pylontech battery. The ESS consists of 3 Multiplus 5000.
I've activated both peak shaving limits with 35A. Today in the morning the total power was around 2 to 3kW and everything was used on AC loads and charing the battery. There were no charging limits and the system was far away from full power. The grid point is 0W and there was no load. I really was wondering when I saw, that the Fronius inverter was throttles to around 1/4 of the possible power. But why? No load on the grid and the battery was far away from the charing limits. After deactivating export current limit it was working again with full power. I could reproduce it by activating it again. The system feed in setting was deactivated, but feed in limiting showed active every time I've activated the export current limit.
Do I miss anything? I believe that there is a bug in the new version.
Regards,
Werner