question

Philip Kamau avatar image
Philip Kamau asked

Lots of flickers on load side during daytime with Fronius setup

I am getting a lot of flickers during the day from my Victron system that has a Fronius inverter AC coupled to it. Currently, a PV support assistant is used to regulate the output of the grid-tied inverter by using frequency control. Can this have an effect on the loads, especially ones connected to UPSs

AC PV Coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·

@Philip Kamau

Common with Fronius PV inverters especially with low light and low load conditions.

With UPS's since they are designed to be fussy about power, the frequency will be messing with their sensitivities.

If you contact them (Fronius) directly they can help with a few deeper settings to smooth it over a bit.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

palom170 avatar image
palom170 answered ·

fro31330upd.zip

Please Install the firmware version 31330

After installing you need to choose the mg50 if you grid is 50hz or 60hz instead.



fro31330upd.zip (11.1 MiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Philip Kamau avatar image Philip Kamau commented ·
Thank you, the system is much better now, still monitoring for flickers
0 Likes 0 ·