Weird behaviour when using multiple VM-3P75CT energy meters

Hi,

I recently bought 2 VM-3P75CT energy meters to measure the PV power installled on the AC-output of an ESS. So both are in the PV-inverter role.

Both are on the same VE.Can to a Cerbo GX. (they are also connected via the ethernet port but that is not used on the cerbo's config)

I noticed a few things that are not what I expected, I guess also a few of them bugs.

  • First: in remote console they both show up (so ok), altough one seems to measure only a fraction about what is happening (I still need to investigate this, any ideas are welcome)

1710923831756.png


  • In VictronConnect under the cerbo in VRM tab, it shows 2 but 2 times the same name with weird values:

1710923765173.png

(under the local tab it is ok, because they are also ethernet connected)


  • In the VRM device list, only one:

1710923963432.png


  • On the VRM firmware tab, I need to press scan, 2 or 3 times before both show up (don't know if this is normal behaviour). Altough this morning this seems to be fixed.


  • Under Modbus TCP services, only 1 shows up (so homeassistant integration also only sees 1)

1710924406244.png


  • Same issue in node-red (only 1 available):

1710924566050.png


Can someone shed a light on this?


Thanx!

Energy Meter
1710923765173.png (103.4 KiB)
1710923831756.png (10.9 KiB)
1710923963432.png (12.3 KiB)
1710924406244.png (13.8 KiB)
1710924566050.png (11.2 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blieve avatar image blieve commented ·

Issue seems to be reintroduced with venusOs v3.33

0 Likes 0 ·
6 Answers
blieve avatar image
blieve answered ·

Apparently a bug in VenusOs sometimes assigning a duplicate VRM instance 0. Victron logged in remotely to do a fix and now it is working as expected.

Will be fixed in a future version

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Duivert NL avatar image
Duivert NL answered ·

did you use VE can terminators on both ends?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blieve avatar image blieve commented ·
yes, I did
0 Likes 0 ·
nickdb avatar image
nickdb answered ·

Don't connect LAN and CAN.

Remove the ethernet and try again.

I am also not sure if the system actually supports two meters in the same PV role. It would be like trying to configure two grid meters. I have asked, hopefully I get an answer.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blieve avatar image blieve commented ·
Unplugging the LAN didn't make a difference.


Seems that support for 2 is possibly only partially implemented (VRM shows them correctly cummulated, device list in remote console also lists 2, but everywhere else only one pops up)

I don't think I have a strange or uncommon situation with 2 AC coupled PV inverters



0 Likes 0 ·
blieve avatar image
blieve answered ·

The false reading is fixed meanwhile. The CT clamp flipped open overnight apparently.


Tried replacing the RJ45 cables & terminators but same result.

I did noticed now that the one meter that doesn't show has the status led blink red (1 time every 20s or something). Don't know what this mean?

It's in the middle of the canbus chain

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blieve avatar image blieve commented ·

The led code is not in the manual:

1710930326180.png


0 Likes 0 ·
1710930326180.png (24.6 KiB)
Duivert NL avatar image Duivert NL commented ·
not sure but that just might be the kWh/impuls indication
0 Likes 0 ·
Show more comments
blieve avatar image
blieve answered ·

Seems that they both use VRM instance 0 when on canbus. Using them via modbus gives them id 40 and 41 and does work correctly.

Don't know if this ID can be changed. Would rather have them both on canbus instead of a bit less stable ethernet

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ton-gans avatar image
ton-gans answered ·

Hi, you can change VRM instance here: Settings, Services, VE.Can port, Devices, Select device you want to change, Device Instance.

Hope this helps.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blieve avatar image blieve commented ·
That's not the correct way to do it, the ID you mention is the can id and should always stay on 0 for ESS systems. The bug is meanwhile solved in VenusOS, so no need to tamper anywhere.