Hi all, I have come across a Issue in one of my customers system.
its a Quattro 24/5000 setup with ess and AC connect PV with a pv outpuut of 5000
Quattro on 508 fw
Cerbo on 3.22
BMS is 123 smart123
latest ess assistant installed
schedule charge set to 100%
Battery at 100%
Solar is exporting 4.57 KW
load is 780 watts'Grid Tie pv is producing 4.8kw
NOW the issue
The battery voltage at times just keeps rising above its set absorption voltage setting of 28v and its BMS setting of 3.5 per cell -
However if I reduce the schedule charge level to 95% then the battery voltage drops back to its correct voltage also when the schedule charge goes inactive it also drops back
Notes
Cerbo is using GUIMods
Of course if you drop the SOC limit to 95% the issue also stops