Multiplus 8000va x 3 in 3 phase output 1 and 2 not working

Hi All,


I have just completed a 3 phase system the specification is below

3 x multiplus 8000va inverter chargers

1 x cerbo gx controller

1 x Cegasa bms contoller

4 x Cegasa Ebrick 175 ultra batteries each at 13.5kwh a piece


WE have installed the system and had the system working on grid failure fine but no charging times.


Set system up with G99 compliance

Set the Ess assistant for the grid charging times.


Now the system when grid loss will not give any output on AC 1 out or AC 2 out .


I have tried to look at other assistants to sort this but i am now at a loss.


The strange thing is it worked on grid loss through AC1 out before i set grid code and Ess assistant?.


Any help appreciated thanks

Kev



Multiplus-IIMultiPlus Quattro Inverter Chargermultiplus in parallel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

You have stepped through the Cegasa/Victron guide to make sure all the inverters are configured perfectly? That each has the assistant loaded and configured.

Is the GX reporting anything in notifications?


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

lovett-electrical avatar image lovett-electrical commented ·

Hi Nick,


i have been through the setting with the Cegasa and victron but when i log in to the remote console it is not showing the cegasa battery.





0 Likes 0 ·
Show more comments