question

graham914 avatar image
graham914 asked

Multiplus 2 ac input

Hi

On multiplus 2 pictures of units, on some of the schematic's on the front panel the AC input line shows 2 relays / contractors in series, where as some pictures of units only show 1.

Why is this.?

Thanks

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Alex Pescaru avatar image
Alex Pescaru answered ·

From some point during time, the safety rules in some countries demand 2 series relays for AC disconnect.

So older units have 1 relay, newer ones 2 relays.